I have an issue where we need to design for (4) receptacles each having 4A on (1) 20A circuit. That means 4A per receptacle (this is the requirement). Problem is we don't have power nearby and have to run 300 ft. When I do a voltage drop calculation, even with #10 (or #8), conductors I have a huge voltage drop. This is expected since we are 120V, but I'm unsure about the current value that should be used. Title 24 (California job) requires you to use the furthest receptacle, but I don't know if I should be using the furthest receptacle at the full 16A load, or just use the draw of the individual receptacle at 4A.
I'm guessing this depends on how the contractor wires it right? If they daisy chain everything then I would depend on where the homerun occurs and how far that is correct?
I'm guessing this depends on how the contractor wires it right? If they daisy chain everything then I would depend on where the homerun occurs and how far that is correct?