Yup that was my next guess. With single phase loads you multiply times 2, for 3 phase you multiply times 1.73. Although most calculators ask you for the ONE WAY distance of the run, because they automatically multiply times 2 for you...

To clarify I wasn't the one that got the low voltage drop. It was another user.

I knew it wasn't you. Sorry if I led you to think that.
 
I used an on line calculator. All the ones that I found used circuit length that had the two conductors already factored in. If hbiss was using a calculator or calculation that did not factor in both the hot and the neutral, the effect would be the same as halving the length of a two wire circuit.

Since his figures are very close to a 150' run that considers both conductors, I was thinking he didn't take the fact into consideration that there were two conductors that needed to be figured in. I remember this happening to many students in my apprenticeship on tests.

I guess I'm confuses as to why 300' wouldn't be used.
The OP indicated the load was 300' away from the source.


JAP>
 
I guess I'm confuses as to why 300' wouldn't be used.
The OP indicated the load was 300' away from the source.

It depends on the formula being used.

300' home run is 600' of wire. Some use a formula that does that part for you. Some don't.

I agree to try to use a multi-wire circuit.
 
It depends on the formula being used.

300' home run is 600' of wire. Some use a formula that does that part for you. Some don't.

I agree to try to use a multi-wire circuit.

I'm old fashioned

2x300x12x16= 115200/41740 (Cm for #4) = 2.76/100 = .03 or 3% Voltage Drop.

I may be all wet on this though.

JAP>
 