good morning i have a question concerning wire size for a 120 volt circuit coming coming from a 240 volt sub panel in a manufacturing plant and running 300 feet to power a gate opener and a gate light . the gate opener has a 115v 11.3 amp motor, the pole light is a high pressure sodiom with a 190 input watts . from my calculation i am coming up with 6 awg to keep the drop within the 3% recomended by the NEC . Would like to know if i am right on my calculation. also, the wire would be fun under ground in conduit .
 
I get #6 AWG also using a load of 13 amps. Since the gate has a motor you want to ensure that the voltage drop isn't very large when the motor starts up. For 240 volts I get #8 AWG.
 
good morning i have a question concerning wire size for a 120 volt circuit coming coming from a 240 volt sub panel in a manufacturing plant and running 300 feet to power a gate opener and a gate light . the gate opener has a 115v 11.3 amp motor, the pole light is a high pressure sodiom with a 190 input watts . from my calculation i am coming up with 6 awg to keep the drop within the 3% recomended by the NEC . Would like to know if i am right on my calculation. also, the wire would be fun under ground in conduit .


THE VOLTAGE TO THE GATE IS 120V
 
THE VOLTAGE TO THE GATE IS 120V

LOOK AT THE MOTOR PLATE AND VERIFY IT CAN'T BE SWAPPED TO 240V.

But, yes, the rest of the controls may matter as well, which is why I simply said to verify that the equipment as a whole couldn't be changed. Some can. A lot of them can. It's worth the look.
 
thanks all i did not considers stepping up the voltage. the data plate says it can be configured to 230 volt. but not sher if i have the room for a double pole breaker.
 
thanks all i did not considers stepping up the voltage. the data plate says it can be configured to 230 volt. but not sher if i have the room for a double pole breaker.

As you do your comparisons, keep in mind that because the current drops and the reference voltage increases, doubling the voltage allows you to use one quarter the size conductors for the same percentage voltage drop.
 