Just do a standard voltage drop calculation.
Roughly 1A of load, 1500 feet of wire, 2.5 ohms per 1000 feet. A bit less than 4V of drop.
The AC formula from Tbl.9 Note #2 gets ~7 volts dropped with Tbl.9 default pf=0.85
If excess capacitance from 1500ft of cable results in negative pf=(-0.01), voltage drop is near Zero, before it hits Ctrl-Panel power supply.
If UL listed control panel uses a class-2 power supply for control voltage, or external wall wort, this inductive reactor may remove branch-circuit capacitance, before feeding control circuits.