What is RMC ? I decided to run #6 Cu through 1 1/2 pvc and a 60 amp panel, which means I have to go deeper, 18 " to top of conduit. Thank you for your suggestions.Another issue that will come up with your plan: you can't run multiple branch circuits or feeders to a separate building (see 225.30) You will need to run a multiwire branch circuit or a feeder to the separate building. This will disqualify the ability to use the 120 volt 20 amp GFCI protected circuit buried at only 12 inches deep.
You could use RMC if you wanted to remain shallow though.
I would just pull THWN through your raceway instead of UF - it will pull much easier.