New Mexico's NMAC 14.10.4 Electrical code uses 2LRI/1000 with I at 80%.
I find 2LRI/P on Mikes Excel spread sheet. For tests purposes here in NM If it does not hint at NM you use the NEC and national info not NMs. No constant is shown on our tests they are as simple as; You have 8 ga THW going 450 feet at 40 amps to a motor at 120V, What is the VD. They are looking for correct math not correct electrical answer so the Formula only matters.
Length = L
Parallel = P
Resistance = R per foot
Current = I
So I get using the NMAC version 2*450*.35*32 (40*.8)/1000 = 10.08 VD
Where the Spread sheet gives me 40*.35*450*2/1= 12600 VD
If I use the per foot value for the resistance I get
2*450*.000778*32/1000 = .02 VD
Spread Sheet says 40*.000778*450*2 = 28.01 VD
And actually using the Spread sheet at 40Amps is 28.01 V
Using the spread sheet with 32Amps (40*.8) is 22.41 V
Which way is right. I never got this answer correct on the test in two times. another monkey in the mess is Telecomm teaches power Techs 2*K*L*I/CM for VD but that is DC only. And we had to carry a constant in our heads for K.
So anyone got a good answer?
I find 2LRI/P on Mikes Excel spread sheet. For tests purposes here in NM If it does not hint at NM you use the NEC and national info not NMs. No constant is shown on our tests they are as simple as; You have 8 ga THW going 450 feet at 40 amps to a motor at 120V, What is the VD. They are looking for correct math not correct electrical answer so the Formula only matters.
Length = L
Parallel = P
Resistance = R per foot
Current = I
So I get using the NMAC version 2*450*.35*32 (40*.8)/1000 = 10.08 VD
Where the Spread sheet gives me 40*.35*450*2/1= 12600 VD
If I use the per foot value for the resistance I get
2*450*.000778*32/1000 = .02 VD
Spread Sheet says 40*.000778*450*2 = 28.01 VD
And actually using the Spread sheet at 40Amps is 28.01 V
Using the spread sheet with 32Amps (40*.8) is 22.41 V
Which way is right. I never got this answer correct on the test in two times. another monkey in the mess is Telecomm teaches power Techs 2*K*L*I/CM for VD but that is DC only. And we had to carry a constant in our heads for K.
So anyone got a good answer?