Voltage drop when sizing equipment ground wire...?
Danny89
Indian Land
So was talking to a journeyman yesterday and the gentleman stated we should upsize our ground wire due to the distance and voltage drop.
Situation 250 feet distance 60 amp branch circuit.
Table 250.122 says #10 Cooper for 60amp.
Should I upsize or does it matter? Is there a code reference if upsizing is a good idea?
Thanks!
Sent from my Moto Z (2) using Tapatalk
Thanks!
Did you upsize the ungrounded conductors because of voltage drop? If not then #10 copper still is acceptable, if you did upsize then the EGC must be increased by same proportion as your ungrounded conductor was increased.
Thanks!
Yes you must up-size if the ungrounded conductors are up-sized too because it's required by the section that Dennis posted. What size ungrounded conductors are you using?
Yes we did upsize to a #4 awg copper
What you need to do is find cross secitonal area of 6 AWG and find out what percent increase there is to 4 AWG, then multiply CSA of 10 AWG by the same percent, your new EGC can not have a CSA smaller than the result.
As a small addendum to this: the code requires you to go by % increase. However because of the way AWG is defined, the same # change gives the same % increase, with one exception.
By definition, the % increase in size from #6 to #4 is equal to the % increase from #10 to #8. However because the values in AWG tables get rounded, you may find situations where if you do the % calculation doesn't match if you use the tables. Since the code specifies % change, the AHJ might permit change by AWG difference or might require change by % difference.
-Jon
Interesting discussion, question, using a 3 conductor Cable TC, current carrying conductors upsized for Vd and integral cable EGC is too small, can a larger single conductor EGC be installed alongside and external to the cable?