The circuit in question is this. I'm pulling 2 legs and a neutral from a 208v 3 phase meter stack to a 100A dwelling unit panel. The breaker feeding the unit is 100A so I'm basing my voltage drop off of 80% of the breaker which would be 80A. So would I use the multiplier of 2 or 1.732 to determine the voltage drop for the sub feed feeding the unit panel?
See my post #19 for more explanation... If the bulk of the loading on this single phase panel is 208V loads, then use a multiplier of 2. If the bulk of the loading is 120V loads, then use a multiplier of 3.46 (1.732 * 2). Reality will be somewhere between the two.
-Jon