hardworkingstiff
- Wilmington, NC
Re: Voltage drop
john,
I'm curious as to how you and I can come up with such different voltage numbers, so I ran the calculations with a different formula. I used VD=I*R (instead of the spreadsheet I have set up). Using 20' of wire (10' there and 10' back) at a resistance of .00193/ft., and the cumulative total of current at each point, I came up with similar results to my spread sheet. What formula are you using?
Looking at the 14th and 15th fixture in your calculations, you have a VD listed as .51 volts and I have it listed as .03 volts. If VD=I*R is valid, the current for 1 lamp (load between 14 and 15 is .08333 amps and the resistance in the wire is (from table 8 in the NEC) .00193 ohms/ft (times 20' of wire, 10' there and 10' return) we get VD=.0833*.0386=.00322 volts dropped between the 14th and 15th fixture.
If you look at the 1st fixture, you get VD=12.5(cumulative amperage of the 15 lamps)*.0386=.4825 volts dropped between the breaker and the 1st lamp. I have this listed as .48 and you have it listed as .2, one of us is using the wrong formula.
john,