ohmhead
Senior Member
- Location
- ORLANDO FLA
I have a panel that the engineer states the demand load is 19 amps its a 42 crt 225 amp 3 phase 480 volt panel.
There is only two breakers used and they are rated at 30 amps each and 3 phase. All the other breakers in panel are listed as spares this is in the panel schedules and its not a mistake .
My question the rule for voltage drop needs the load in amps to calculate the drop. So does the NEC just go by the actual load at the time of calculation?
I feel a 225 amp panel with 42 crts can be loaded and trip in the future what's your thoughts . As far as voltage drop when calculated at 19 amps demand its ok but if its loaded high it will drop the voltage down below the 3% or 5% required. I also feel its a poor design as the breaker feeding this panel is a 225amp.
So how does the rule on voltage drop work is it the load in amps that rule at that moment in time ?
There is only two breakers used and they are rated at 30 amps each and 3 phase. All the other breakers in panel are listed as spares this is in the panel schedules and its not a mistake .
My question the rule for voltage drop needs the load in amps to calculate the drop. So does the NEC just go by the actual load at the time of calculation?
I feel a 225 amp panel with 42 crts can be loaded and trip in the future what's your thoughts . As far as voltage drop when calculated at 19 amps demand its ok but if its loaded high it will drop the voltage down below the 3% or 5% required. I also feel its a poor design as the breaker feeding this panel is a 225amp.
So how does the rule on voltage drop work is it the load in amps that rule at that moment in time ?