Re: Voltage Drop
In a 120 volt system, the suggested limit of 3% voltage drop (for a branch circuit) equates to 3.6 volts. Plugging this value into Dereck?s formula, I get a result of 31,500 CM. The smallest conductor that is at least this big is a #4 (41,740 CM).
But what exactly do you mean by calling this a ?20 amp load?? Do you mean that you intend to use a 20 amp breaker, or that the devices connected to this load will really draw every bit of 20 amps? The difference is that for a 20 amp breaker, you should limit the actual load to under 16 amps (80%). Using an actual load of 16 amps in Dereck?s formula gives a result of 25,227 CM. In that case, a #6 is sufficient (26,240 CM).