A question from my Mike holt book,
A 240v,24A,single phase load is located 100 ft from the panel board and is wired with 10AWG. What is the voltage drop of the circuit conductors?
Answer in book is 5.76V
1.20 ohms per 1000 foot the calculation result says.
10awg 1.240 ohms per 1000 ft
1.240÷1000=.00124
.00124×200ft=.248
.248 ×24A=5.952.
Why does the book round the numbers.