What is the voltage drop of a 90' run of:
14 AWG NM
12 AWG NM
10 AWG NM
Thank you for your help!
14 AWG NM
12 AWG NM
10 AWG NM
Thank you for your help!
2002 NEC 215.2 (A)(4)FPN No. 2:Conductors for feeders as defined in Article 100, sized to prevent a voltage drop exceeding 3 percent at the farthest outlet of power, heating, and lighting loads, or combinations of such loads, and where the maximum total voltage drop on both feeders and branch circuits to the farthest outlet does not exceed 5 percent, will provide reasonable efficiency of operation.
Actually Hbliss, voltage drop is expressed as a percentage all the time. The meaning and understanding is as a percentage of the nominal voltage. Additionally, if you take a look at Awwt's past posts, he makes a lot of sense on them, this is just an area where he needs some work. I am considered an expert on the Code but, I assure you, I don't know it all. I know of no one who does know it all. Many of us have a good handle on parts of the Code and theory.Well, I don't know what kind of training you had but this is simple ohm's law that you should have had on day one. There is NO way that voltage drop on a piece of wire can be expressed as a percentage. None. Percentage implies a reference to 0% or 100%. What would 0% or 100% in this case be?
OK, Bennie: Your answer caused me the most confusion, but it also somehow alerted me that I needed to furnish amps too. My knowledge is deep and long, but it's old, dusty, and rusty. Thank you for bearing with me while I shake off the cobwebs. I know all this stuff, I just need to re-visit it and refresh my memory.Originally posted by bennie:
To calculate voltage drop you must know two of the three values that make up the circuit.
The size and length of the conductors will determine the resistance. One more value must be known.
Voltage drop is "eye times are". You only furnished the "are".