Voltage Drop

Status
Not open for further replies.

rrrusty

Senior Member
Location
Colorado
(Existing)On an underground feed from the pole to the structure with the distance at 735' using Alum direct burial cable sized at 300 kcml with the c/b at the pole at 200A and put on main lugs at the l/c at the structure; What would be the allowable ampacity to carry the structure? My thought was to put a 125A main c/b instead of the lugs in place now,the owner has a 100A going to the main structure as well as a 50A going to a detached garage and wants to add an electric H2O htr and a hot tub; the load calc that I came up with for the main structure is at 86A before he adds the extras; Are my figures and methods off? I had figured that with the distance and v/d that only 125A could be about the max amount; Comments please, Thanks
 
Re: Voltage Drop

the load calc that I came up with for the main structure is at 86A before he adds the extras;
Is this 86A load at 120V or 240V? In other words, are all of the loads single phase-single pole or are some single phase-two pole?
 
Re: Voltage Drop

It is on a 240V calc; It has 3- 2pole circuits; Range, dryer, H2O pump Then the rest are 1pole circuits
 