(Existing)On an underground feed from the pole to the structure with the distance at 735' using Alum direct burial cable sized at 300 kcml with the c/b at the pole at 200A and put on main lugs at the l/c at the structure; What would be the allowable ampacity to carry the structure? My thought was to put a 125A main c/b instead of the lugs in place now,the owner has a 100A going to the main structure as well as a 50A going to a detached garage and wants to add an electric H2O htr and a hot tub; the load calc that I came up with for the main structure is at 86A before he adds the extras; Are my figures and methods off? I had figured that with the distance and v/d that only 125A could be about the max amount; Comments please, Thanks