Voltage drop

stretch12

Member
Location
taxachusetts
I’m trying to figure voltage drop on a resi service 120/240 single phase . Distance is approximately 2k ft from xformer to residence. Figuring on al conductors, the south wire app is showing ridiculous amount of parallel conduits. I haven’t done one of these calculations in like 15 yrs. And am having the largest brainfart of my life trying to get started.
Any assistance or insight, very much appreciated.

Chris
 
2000' is probably going to need a step up to MV. You could try just going to 600. I used to say dont mess around with 600, just go to MV, but with the cost of CN cable and MV transformers doubling in the last 6 years, sometimes there is a sweet spot for 600V. For budgeting, T&R has 25 kva pad mounts for $6500, and #2 AL CN primary is about $3.75 last time I priced it (you inly need one cable for single phase). Dont forget 2 transformer pads, prolly $800 each
 
I ran the numbers with the Southwire VD calc and it said 3 sets of 750 kcmil aluminum for 3% VD. Switch to copper and it's 3 sets of 500 kcmil.
If 25 kVA is a suitable transformer size, which is only 104A @ 240V, wouldn't the comparable voltage drop calculation be based only on 104A? E.g. 6 sets of 250 kcmil Al per Southwire.

Cheers, Wayne
Rob for 600v? I get one set of 3/0 AL for 18kw at 600V (75A at 240). Bump up to 250 and you get 100A under 3%.

I get $25,000 in conductor, 3 sets of 350 AL for 75 amps at 240.
 
If 25 kVA is a suitable transformer size, which is only 104A @ 240V, wouldn't the comparable voltage drop calculation be based only on 104A? E.g. 6 sets of 250 kcmil Al per Southwire.

Cheers, Wayne
In general i would use 100 amps or less for a VD calc for a dwelling. A 25kva transformer with around 75A load for VD purposes is usually about right.
 
Rob for 600v? I get one set of 3/0 AL for 18kw at 600V (75A at 240). Bump up to 250 and you get 100A under 3%.

I get $25,000 in conductor, 3 sets of 350 AL for 75 amps at 240.
Let me go back and check. I might have kept the 320 amp current value.
 
I kinda have the feeling , that a service calc then work on vd. We are at the stage jus spitballing #s just know it’s gonna be a 400a se, it’s a big home.
 
Yes. You can't do a voltage drop calculation without first understanding the current that will be drawn.

But what you should do for your 'spitball' calculations is calculate solutions for 400A, 100A, 50A, and 25A, just to get a rough idea of costs. Also get the power company to price out bringing primary to a transformer near the house.

The different costs of these different service values will help you decide how to approach the problem.

Something else to keep in mind is that residential electrical service is very variable; you may have high peaks but a low average. Often the issue with voltage drop is that you don't want apparent effects (lights flickering, UPSs triggering) when some large load kicks in. So sometimes you are better off putting money into reducing the magnitude of large load inrush, for example by using inverter fed HVAC systems or well pumps.

Depending upon the utility tariffs, this might be one of the rare cases with off grid solar makes sense.
 