Just understand that actual draw will be a lot less than a NEC load calc will show, and a lot less than you would think, even if its a "big home". I am guessing that maybe a 600 volt step up step down might be the ticket for your application. Even if you go with 200 amps actual load (which would almost be certainly way Overkill) you would need (2) 500 AL (use the exception for using the grounded conductor as your bonding conductor so no EGC needed) so you are looking at a total of about $4.75 /foot. Thats $1 / foot more than 15 kv MV cable, but MV transformers will be $8000 more. MV is great but many people are scared of it and dont want to get the tools to make up the elbows.I kinda have the feeling , that a service calc then work on vd. We are at the stage jus spitballing #s just know it’s gonna be a 400a se, it’s a big home.