Determine wire size necessary for both 125% motor current and say 3% voltage drop. Use the larger of the two results.Pushpin said:When sizing motor feeders......you must size them 125% of the motor current. If this covers the voltage drop problem do you need to use a larger size wire? Or should you calculate the wire size / voltage drop based on 125%?:-?
Dave_PE said:hmspe.......
Depends what State you are working in.....the Florida Building Code limits VD to 2% for feeders, 3% for branch circuits.
Along the lines of iwire Bob's interest, I'm wondering if the Florida Building Code makes any distinction between subpanel feeders and motor feeders...?Dave_PE said:hmspe.......
Depends what State you are working in.....limits VD to 2% for feeders, 3% for branch circuits.
13-413.1ABC.1 Voltage drop.
13-413.1.ABC.1.1 Feeders.
Feeder conductors shall be sized for a maximum voltage drop of 2 percent at design load.
13-413.1.ABC.1.2 Branch circuits.
Branch circuit conductors shall be sized for a maximum voltage drop of 3 percent at design load.
iwire said:When this same criteria is applied to an entire service it will become artificially high standard to meet.
bphgravity said:From Chapter 13 of the Florida Building Code:
hardworkingstiff said:How many wire sizes increase would you expect for the feeders?
Yea, the NEC should allow better demand factors.iwire said:All I am saying is that the NEC service calcs result in a number much larger than the actual load will be.
Dave_PE said:...the Florida Building Code limits VD to 2% for feeders, 3% for branch circuits.