You left out a lot of application specific data to allow any meaningful answers.
80VAC is an uncommon supply voltage. I've never heard of it. Are you sure that is what is required?
What is the actual voltage, current, number of phases, frequency you are trying to deliver?
An example of how you might do this for say 120V, 1ph, 60hZ, 20A, 2400':
1. Get 2 each 2.5kva 120V/600V transformers - at least one rated for step-up.
2. Connect step-up xfm to 120VAC 20A circuit, stepping up to 600V.
3. Run 2400', 2 conductor, #8 out to the area.
4. Connect second xfm step-down to 120V.
carl