hotrodnhra
New member
i have a 30amp service to an airplane hanger with a 30 amp main. the inspector wants me to upsize to #6 for voltage drop ok but he wants the grounded conductor to be upsized to a # 6 also. can anyone clarify this for me. thanks
i have a 30amp service to an airplane hanger with a 30 amp main. the inspector wants me to upsize to #6 for voltage drop ok but he wants the grounded conductor to be upsized to a # 6 also. can anyone clarify this for me. thanks
Grounded conductor or grounding conductor?
For what it is worth the NEC has no section requiring up sizing the feeder for voltage drop so unless there is a local amendment you should be able to say no.
no section ? 647? 695 ?![]()
i the inspector wants me to upsize to #6 for voltage drop ok but he wants the grounded conductor
According to 250.24(C)(1) the smallest neutral he could have is a #8, if he used #6 service entrance conductors.Read art. 250.122(B) if you do decide to upsize but better still upsize to #6 conductors and a #10 ground and put a 60 amp breaker on it. Bet that'll make him/her mad
I tried a PM asking him to calrify perhaps we will see
it being post #1, I was shooting in the dark thinking he might not know of 250.122.... he would not be alone
According to 250.24(C)(1) the smallest neutral he could have is a #8, if he used #6 service entrance conductors.
Something isn't right with all this...
The code requires oversizing for voltage drop so that the total voltage drop, that is feeder + branch circuit does not exceed 5%.
The code requires oversizing for voltage drop so that the total voltage drop, that is feeder + branch circuit does not exceed 5%.
Article 215.2(A)(3) FPN No.2 is for branch circuits and article 210.19 FPN No.4 is for branch circuits.