For 24 volt fire alarm systems, a vast majority of notification appliance manufacturers have appliances listed to operate as low as 16 volts, exceeding the requirements of NFPA 72-2010 section 10.14.12010 NFPA 72 article 10.14.1 requires fire alarm equipment to work with 85% to 110% of listed voltages
Therefore, the voltage on the NAC would be permitted to drop to a minimum of 16 volts before violating the requirements of NFPA 72-2010 section 10.14.2.4, correct?and 10.14.2.4 requires installations to fall in the manufacturer's voltage requirements. That would mean a maximum voltage drop to 20.4 volts on a 24 volt system.