Using Southwire VD calculator:
2 conductors per phase utilizing a #600 Aluminum conductor will limit the voltage drop to 2.70% or less when supplying 400.0 amps for 600 feet on a 480 volt system.
2 conductors per phase utilizing a #500 Aluminum conductor will limit the voltage drop to 3.02% or less when supplying 400.0 amps for 600 feet on a 480 volt system.
2 conductors per phase utilizing a #350 Aluminum conductor will limit the voltage drop to 3.85% or less when supplying 400.0 amps for 600 feet on a 480 volt system.
1 conductors per phase utilizing a #1000 Aluminum conductor will limit the voltage drop to 3.24% or less when supplying 320.0 amps for 600 feet on a 480 volt system.
I wouldn't get stuck on the 3%. It's only a guideline, also, the max. current in the cable is 320A not 400A, assuming your using a 400A that is not 100% rated.