A aj_ales Member Oct 20, 2005 #1 Where can i find in the NEC-2002 the maximun voltage drop allowd in a feeder?
J jtester Senior Member Location Las Cruces N.M. Oct 20, 2005 #3 Re: Voltage drop Remember that FPN's are not enforceable as part of the NEC in general. Basically, the NEC doesn't mandate specific voltage drops. Jim T
Re: Voltage drop Remember that FPN's are not enforceable as part of the NEC in general. Basically, the NEC doesn't mandate specific voltage drops. Jim T
peter d Senior Member Location New England Oct 20, 2005 #4 Re: Voltage drop Voltage drop is a design issue, not a safety issue. That's why there are no code rules addressing it. That said, it's in your best interest to minimize voltage drop for performance reasons, to meet job specs, etc etc..
Re: Voltage drop Voltage drop is a design issue, not a safety issue. That's why there are no code rules addressing it. That said, it's in your best interest to minimize voltage drop for performance reasons, to meet job specs, etc etc..
P Physis 2 Guest Oct 21, 2005 #5 Re: Voltage drop Typically you have 10% tolerance to work with. The utility gets 5% of that and you try to splitt your 5% up by keeping the feeders and service conductors under 2% and the branch circuits under 3%.
Re: Voltage drop Typically you have 10% tolerance to work with. The utility gets 5% of that and you try to splitt your 5% up by keeping the feeders and service conductors under 2% and the branch circuits under 3%.