Re: Voltage Imbablance
Nearby capacitor banks have been known to cause bus overvoltage trips on drives. When the capacitor closes in there is a momentary short circuit (microseconds) then a ringing transient will occur (usually only lasting about 1/2 cycle). This is normal to the operation of caps and a 3% line reactor in front of the drive will dampen the problem. To verify this you would need a power quality analyzer that is capable of capturing waveforms with at least a 64 micro second response time.
The power quality engineer should be able to tell if you have a bad neutral connection if the connection is upstream of the monitor. Otherwise it was most likely an event on one phase of the 3 phase distribution system. This will cause the other two phases to swell, momentarily while the fuse blows and opens the faulted circuit.
Nearby capacitor banks have been known to cause bus overvoltage trips on drives. When the capacitor closes in there is a momentary short circuit (microseconds) then a ringing transient will occur (usually only lasting about 1/2 cycle). This is normal to the operation of caps and a 3% line reactor in front of the drive will dampen the problem. To verify this you would need a power quality analyzer that is capable of capturing waveforms with at least a 64 micro second response time.
The power quality engineer should be able to tell if you have a bad neutral connection if the connection is upstream of the monitor. Otherwise it was most likely an event on one phase of the 3 phase distribution system. This will cause the other two phases to swell, momentarily while the fuse blows and opens the faulted circuit.