voltage limit for "low voltage" landscape lighting
RustyShackleford
NC
electrical engineer
Very simple question, which I should know ... but do not, never having worked on voltages higher than 12v and lower that 110-120vac.
How high a voltage is acceptable for "low voltage" lighting, landscape lighting in particular ?
Article 411 suggests the limit is 30v (or 42v "peak", presumably meaning 30 RMS AC is ok).
Landscape lighting is clearly a "wet area".
For this project, I'm interested in ripple-free DC only.
No one seems to care, but FWIW ...
I actually emailed a UL guy, and he got back to me, telling me that (for wet locations) 30v is the limit for "pure DC", which seems to be defined as the peak-to-peak ripple being less than 10% of the DC voltage. The max for sinusoidal AC is 15v.
He says this is in UL1838 (see below), and also in a note to Table 11B of the NEC (presumably not the 2011 version, which is where I was looking).