OK. So I happened to be in the area, and for some reason the inspector butt dialed me, so I met him at the house.
He had the ct cab cover off and noted the rust on the cabinet where the neutral lugs are bonded to (which I mentioned I couldn't see or get to because the cabinet was locked)(and all the lugs are intact and touching).
He also mentioned the gec at the water meter may be rusty (which it may be but I've seen worse and all is tight).
He also noted that the service has no ground rod (ok, there is non.).
His thought is that there is or may be a loss of ground. (??? if there was a loss of ground at the premises, shouldn't I have still read 240v, especially when I turned off the panels??)
He also took the meter and measured 120/240 in the ct cabinet. I took the meter and measured 120/240 at the cabinet and one of the panels. I also measured 120v hot to water pipe.
He said he didn't touch anything.
I mentioned this is the first time I saw the 240v.
I held the tester and he banged connections with his pliers. 240v stayed.
So at this point he suggested to continue with the work order and have engineering monitor the voltage, that it couldn't hurt.
I tested my meter and it works. I know what I saw.
I guess I will stand down till/if/when I hear something.
argh, feel like the boy who cried wolf.
He had the ct cab cover off and noted the rust on the cabinet where the neutral lugs are bonded to (which I mentioned I couldn't see or get to because the cabinet was locked)(and all the lugs are intact and touching).
He also mentioned the gec at the water meter may be rusty (which it may be but I've seen worse and all is tight).
He also noted that the service has no ground rod (ok, there is non.).
His thought is that there is or may be a loss of ground. (??? if there was a loss of ground at the premises, shouldn't I have still read 240v, especially when I turned off the panels??)
He also took the meter and measured 120/240 in the ct cabinet. I took the meter and measured 120/240 at the cabinet and one of the panels. I also measured 120v hot to water pipe.
He said he didn't touch anything.
I mentioned this is the first time I saw the 240v.
I held the tester and he banged connections with his pliers. 240v stayed.
So at this point he suggested to continue with the work order and have engineering monitor the voltage, that it couldn't hurt.
I tested my meter and it works. I know what I saw.
I guess I will stand down till/if/when I hear something.
argh, feel like the boy who cried wolf.