Re: voltage on gnd wire.
So I just took a 250' coil of 14-2 and put a plug on the end with bonding jumper across the n and G ( i a m doing this at my own house) I then applied a 500 watt load and got the same efecct as at my customers house, 50+ volts from disconnected ground to the neutral. I will assume this is the same problem at my customers house. I will t-shoot this week.
My question is I had voltage from a disconected ground to the neutral on a properly wired circuit as well, I assume this voltage is induced or phantom. How can you tell the difference between "phantom" and real volts using a digital meter. ( my wiggie does not pick up the problem voltage on the N/G bond circuit)

So I just took a 250' coil of 14-2 and put a plug on the end with bonding jumper across the n and G ( i a m doing this at my own house) I then applied a 500 watt load and got the same efecct as at my customers house, 50+ volts from disconnected ground to the neutral. I will assume this is the same problem at my customers house. I will t-shoot this week.
My question is I had voltage from a disconected ground to the neutral on a properly wired circuit as well, I assume this voltage is induced or phantom. How can you tell the difference between "phantom" and real volts using a digital meter. ( my wiggie does not pick up the problem voltage on the N/G bond circuit)