How about we get back to basics?
Here is what I would do.
Now if the both the N to L1 and N to L2 voltages remained fairly steady I would have to rule out a neutral problem.
However if both L to N voltages where changing I would continue on my pursuit of a neutral issue somewhere between the panel and the secondary side of the transformers.
This is not complicated, it is simple straight forward trouble shooting we do all the time.
Here is what I would do.
- I would shut the panel down
- I would carefully lift any GEC connections and isolate them from the neutral
- While the panel was off I would measure voltage on the line side of the main
- L1 to N
- L2 to N
- L1 to L2
- Note the readings
- Now leaving L2 and any two pole loads off I would load L1 as much as possible and take the readings
- L1 to N
- L2 to N
- L1 to L2
- Note the readings
- Now leaving L1 and any two pole loads off I would load L2 as much as possible and take the readings
- L1 to N
- L2 to N
- L1 to L2
- Note the readings
Now if the both the N to L1 and N to L2 voltages remained fairly steady I would have to rule out a neutral problem.
However if both L to N voltages where changing I would continue on my pursuit of a neutral issue somewhere between the panel and the secondary side of the transformers.
This is not complicated, it is simple straight forward trouble shooting we do all the time.