Voltage on Nuetral?
In a typical American,400amp feed,120v,60hz,2-phase panel for home use. What should the total Neutral return voltage be?
I've wondered this ever since I returned from Germany where I was an Electrician for the USAF.
Re: Voltage on Nuetral?
Chris,
the problem is, this is not typical and a "neutral" wouldn't exist in it's true meaning if it were a typical system.
If we are looking at a typical 120/240 v single phase system, (one winding center tapped) the neutral should have no voltage in theory.
Roger
[ January 20, 2005, 08:41 PM: Message edited by: roger ]
The neutral voltage depends on - neutral to what? If you measure neutral to ground at a service disconnect, you better read nearly 0 volts. On the other hand neutral current won't flow without accompanying voltage drop. A 120 volt single phase voltage drop calculation includes distance x 2, or circuit length down and back, or phase voltage drop plus neutral voltage drop. Neutral voltage depends on where your other reference is.
Jim T
My meaning was at the service disconnect. By the way I'm glad I stumbled across this forum. I've already looked over several of the postings and this is the most informative forum I've come across.
you may have some voltage to ground on a neutral. I commercial we can typically have 1 to 3 volts, and not worry too much about it. Over that the electronics tend to see it.