I'm looking for the formula to calculate primary to secondary voltage ratio as required in 240.21(C) (6).....:-?
Primary to secondary is 480 to 120, not 480 to 208. We are comparing (creating a ratio) a phase to a phase, not a phase to two phases. Assuming a delta wye transformer.
Not this one. Was just reading along - not paying any attention - just nodding my head. Hit ryans post, blinked, saw the windings in my head and thought, "Yep, right on, that's the way they are wound - glad one of us was awake."...Lets see how the engineers kill me on this one...![]()
Man, I thought I was just starting to understand it and Jon throws a wrench in the works. :grin:
It's all good, by the time this thread is done I will have learned a few things.![]()
I've got to throw in with infinity. There's a turns ratio and a voltage ratio. The voltage ratio is the ratio of ?-? voltages of the transformer. The turns ratio is the ration of individual windings.
FWIWGonna disagree here.
...IMHO the ratio is 2.31:1
There's a turns ratio and a voltage ratio.
Now I am getting it. :smile:
so, 240.21.c.6.1 is 2.31 x (primay OCP/3)= min ampacity secondary conductor, right?
That's the way I read it.billsnuff said:so, 240.21.c.6.1 is 2.31 x (primay OCP/3)= min ampacity secondary conductor, right?![]()