I still think turns ratio and voltage ratio are one and the same. Here is an interesting article on the subject (not saying it is right or wrong, as I know not who wrote it): http://www.tpub.com/content/doe/h1011v4/css/h1011v4_49.htm
Secondary phase current = 480V * 100 A / 120*1.732 = 231 A
thanks
That's what came to my mind.480V ? 100A ? 208V = 231A
That's what I finally figured out. The coils are wound just the way you daid, but that's not the current flow the NEC is concerned with. The current ratio is as your buddy said.... He told me I am dead wrong, and that you guys are right. ...
It's correct to a first approximation.I still think turns ratio and voltage ratio are one and the same. Here is an interesting article on the subject (not saying it is right or wrong, as I know not who wrote it): http://www.tpub.com/content/doe/h1011v4/css/h1011v4_49.htm
The calculation relates the secondary current to the primary current for comparison of the secondary conductor ampacity with the primary protection rating. I don't understand the multiplication by one-third the rating of the overcurrent device, though. Seems like it should be the other way around. Say you have a 4160-480 transformer with a 100A fuse in the primary. You would need an ampacity of 100?4160/480/3 = 289A for the secondary. If you actually had 300A in the secondary, you would only have 35A in the primary and the fuse wouldn't come close to blowing.Ok, so can anyone explain why we need to do this calculation and what does it really mean when using secondary conductors up to 25' long?
The calculation relates the secondary current to the primary current for comparison of the secondary conductor ampacity with the primary protection rating. I don't understand the multiplication by one-third the rating of the overcurrent device, though. Seems like it should be the other way around. Say you have a 4160-480 transformer with a 100A fuse in the primary. You would need an ampacity of 100?4160/480/3 = 289A for the secondary. If you actually had 300A in the secondary, you would only have 35A in the primary and the fuse wouldn't come close to blowing.
I still think turns ratio and voltage ratio are one and the same. Here is an interesting article on the subject (not saying it is right or wrong, as I know not who wrote it): http://www.tpub.com/content/doe/h1011v4/css/h1011v4_49.htm
It's correct to a first approximation.
For a practical transformer, voltage ratio and turns ratio are not quite the same.
I'll try.Care to elaborate?
I'll try.
If you increase the load on the output of a transformer, its output voltage will drop due to its impedance. Thus, the input to output voltage ratio will change.
If the transformer is designed to produce rated output voltage at rated load, then the primary to secondary turns ratio has to be slightly lower than the stated voltage ratio to achieve this.
So, on load you get less than rated output voltage.At least in the USA, transformers are not designed to produce rated voltage at rated load.
I'll try.
If you increase the load on the output of a transformer, its output voltage will drop due to its impedance. Thus, the input to output voltage ratio will change.
If the transformer is designed to produce rated output voltage at rated load, then the primary to secondary turns ratio has to be slightly lower than the stated voltage ratio to achieve this.