kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
Has he confirmed it is a three wire cable straight from house panel to garage? Part of why I asked for more clarification of what is there. He said it is very old install - maybe at one time was a "chicago three way" setup and never had an EGC?In his first post the OP says he is dealing with cable feeding a 100 amp panel in a detached garage. In another post he says it's three wires. If the three are as you say, then there should only be 120 in the garage, no 240, and we don't know that for sure.
IMO we have not ruled out some possibilities that maybe never would have had an EGC to begin with.
May ultimately still end up replacing the wiring between the two buildings, but is nice to know what you have and not just guess what the problem may have been. I'd be ensuring I did/did not have continuity through all three conductors before assuming one of them is lost/disconnected, to do that you need to be positive you are not missing a junction box/splice point somewhere as well, or there may be more components of the circuit that need looked into.