Does the Code admit that a voltage stabilizer can also be used for reduction in energy usage in a building?Thanks
Does the Code admit that a voltage stabilizer can also be used for reduction in energy usage in a building?Thanks
They are helpful in a few cases where you have severe voltage imbalances and the lowest is still within tolerance, but otherwise they have the potential to do more harm than good, because a much more likely scenario is that one voltage level is significantly low, not high, so you end up bringing all down to that low level. These scammers operate on the knowledge that most people understand very little about electrical power distribution or use and are desperate to reduce energy costs, so they will believe any good story.
:slaphead:
Good for the power company, not for the consumer.Actually,some power companies effected significant saving in energy consumption by reducing the grid voltage.
Good for the power company, not for the consumer.
When a utility does a system wide voltage reduction, the total kW may go down (temporarily) from their prespective. But at each individual point of use, that reduced voltage can have very negative effects on the equipment. AC induction motors will lose torque, increase slip and still attempt to put out the power required to do the work they are designed to do. That means higher current and more heat in the motor. DC motors will slow down. Power Supplies will run hotter. Air Conditioning systems will have less capacity, so will have to run longer to do the same cooling capacity. Incandescent lighting and resistive heating systems will use less power during the voltage lowering period, but the output will be less. So for many of these point of use systems, whatever they do will take longer which means the kWh will be the same, just the production values per hour will drop for the user. So the utility gets the same NET revenue for the energy they produce, but the end users get less productivity for it and increased maintenance.How so? The lessons learned by the power company in this case may be applicable to the individual consumers.
When a utility does a system wide voltage reduction, the total kW may go down (temporarily) from their prespective. But at each individual point of use, that reduced voltage can have very negative effects on the equipment. AC induction motors will lose torque, increase slip and still attempt to put out the power required to do the work they are designed to do. That means higher current and more heat in the motor. DC motors will slow down. Power Supplies will run hotter. Air Conditioning systems will have less capacity, so will have to run longer to do the same cooling capacity. Incandescent lighting and resistive heating systems will use less power during the voltage lowering period, but the output will be less. So for many of these point of use systems, whatever they do will take longer which means the kWh will be the same, just the production values per hour will drop for the user. So the utility gets the same NET revenue for the energy they produce, but the end users get less productivity for it and increased maintenance.
With resistive heating you have not reduced the amount of energy required to make the heat. You have just spread the energy use over a longer period of time. The cost to user does not change.The subject power company dealt with a grid system of predominantly resistive loads and whatever savings they realized were in turn realized by their customers in proportion.As for the increased maintenance and other costs,they could be set off against the total savings of individual customers with a net positive energy savings.What more is required?
The subject power company dealt with a grid system of predominantly resistive loads and whatever savings they realized were in turn realized by their customers in proportion.As for the increased maintenance and other costs,they could be set off against the total savings of individual customers with a net positive energy savings.What more is required?