Greetings to all,
For the past two weeks, we are experiencing voltage unbalance after few days of bad weather.
Our main transformer is a 5000KVA delta to wye with primary voltage 38kv and secondary voltage 8.32kv. Then, each building have step down transformer from 8.32kv to 480/277v.
To please the power authority, we tested our main transformer (insulation, turn ratio, etc), feeders megger, performed thermal images to the substation, etc resulting in satisfactory result.
After this, the Power Authority began testing the primary voltage resulting in a voltage unbalance of approx. 5.5% in the entrance of our facility (with and without the load of our plant). Also, they performed thermal imaging from their substation to ours resulting only in one hot spot in one feeder connection at the entrance of our facility. They corrected this issue but the unbalance persists.
The voltage unbalance is affecting several motors (i.e chillers, centrifugal pumps) and not permitting to start because of protection.
Another facility in the same primary line has the unbalance but not phase to phase but phase to ground
Any suggestion of any other possible cause?