I have a 120/240 V 3 wire overhead service with the following. Voltage measured at POCO mast connection L1-L2 230V L1-Neutral 114V L2-Neutral 116V.Inside the house I have in the panel at the main lugs L1-L2 220V L1- Neutral 100V L-2 -Neutral 118/120V. I am unable to pull the meter to check voltage there due to a POCO lock that has been installed for whatever reason. Can a faulty meter be causing this type of abnormal reading? Owner tells me that several light bulbs burned out all at the same time and that lights dim considerably when she starts the electric dryer. I was to this house about a week ago and added a dedicated laundry circuit, I did not check the voltage I simply verified the install with a 3 eye GFCI tester. Seems as if it were a neutral problem it would show up when metering the hot legs in the panel. Any thoughts?