Checking voltage In a building .A to b phase 240 volt
A to ground 235 volt
B to c phase 243 volt
B to ground 246 volt
C to a phase 242 volt
C to ground 10 volts
What type of service is this .
 

TheCrow

Member
Location
Mk
Occupation
Electrical
The service is connected to a transformer feeding a panel with a neutral . Wanted to see if a generator can be connected with a manual transfer switch .
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
The service is connected to a transformer feeding a panel with a neutral . Wanted to see if a generator can be connected with a manual transfer switch .
If this is the case, something is definitely wrong. 240V delta would only have a Neutral if it were a "high leg" system, which is usually B phase, so A-C phase is split with a grounded center point to make 120V from A or C to N.

If C is at nearly ground potential, that winding is ether shorted, or someone put in a Corner Grounded Delta transformer, in which case there would NOT be a Neutral at all to connect to that panel.

One way or another, this is messed up.
 

LadyDi

Member
Location
Lubbock, Texas
Occupation
Electrical Contractor, Master Electrician, BA Texas Tech University, College Instructor: Electrician Education
Clear the fault before considering adding anything to the panel. Otherwise, risk injury or death.
 