brother said:what is the formula for voltage drop?
Save yourself some trouble and use this online VD calculator
http://www.elec-toolbox.com/calculators/voltdrop.htm
brother said:what is the formula for voltage drop?
charlie b said:
Sorry, but I do not understand the question.
If you are asking about the performance of a load calculation, then (from Article 220) you assign 180 VA for each duplex receptacle.
tryinghard said:How many general use receptacles would you install in a non-dwelling 20A circuit?
Dennis Alwon said:I was suggesting 5 amps but I was giving that as an example. Yes I do agree that you are limited to 13 receptacles on a circuit.
Dennis Alwon said:I would base it on 3 watts per sq. foot.