Second attempt, got 4 correct. Damn the luck. OK, I need to know where I am going wrong on motor loads in va. The question on the test was for six motors. Three single phase with one motor intermittent 5-minute rated. And three three phase motors with one of them also intermittent 5-minute rated. 460 volt delta with 120/240 transformed at the service. I could not seem to match any of the four choices no matter which way I tried. I used the table 430.148 to get FLC amps for the single phase and table 430.150 to get FLC amps for the three phase motors. The test gives you the motor nameplate values for FLC amps but I learned that nameplate is only used to size overloads so I ignored the nameplate values to determin load. For the intermittent motors I used the demand factors from table 430.22(E), intermittent 5-minute rated, the factor is 85%. Here is how I did the calc's:
single phase;
115v, 2hp=24amps I x E = 2760va
230v, 5hp=28amps(int. 5min) I x E x.85= 5474va
230v, 71/2hp=40amps I x E = 9200va
three phase;
460v, 5hp=7.6amps I x E x 1.732= 6055va
460v, 20hp=27amps(int) I x E x 1.732 x.85= 18285va
460v, 40hp=52amps I x E x 1.25= 51787va
TOTAL VA 93561
Is there a flaw here in my logic? I even dropped out the 1.25 factor on the largest motor and still could not match one of the four answers on the test. Any ideas or help would be great, I would like to pass this thing on the next try. thanks.
single phase;
three phase;
TOTAL VA 93561