1793 Senior Member Location Louisville, Kentucky Occupation Inspector Nov 18, 2008 #21 aftershock said: I would treat it like a 4500 watt water heater. 10/2 romex on a 30 amp breaker. Click to expand... Agreed......
aftershock said: I would treat it like a 4500 watt water heater. 10/2 romex on a 30 amp breaker. Click to expand... Agreed......
frizbeedog Senior Member Location Oregon Nov 18, 2008 #22 Jim W in Tampa said: not going to truck for book its like 50 degrees outside. Paste it Click to expand... Ohh, Chilly! 424.3 (B) Branch Circuit Sizing. Fixed electric space-heating equipment shall be considered a continous load. Click to expand...
Jim W in Tampa said: not going to truck for book its like 50 degrees outside. Paste it Click to expand... Ohh, Chilly! 424.3 (B) Branch Circuit Sizing. Fixed electric space-heating equipment shall be considered a continous load. Click to expand...