- Location
- New Jersey
- Occupation
- Journeyman Electrician
Someone asked me today about the branch circuit for a 10kw, 240 volt, thermostatically controlled electric garage heater. I immediately said 60 amp circuit. Then when I looked in the codebook I thought well maybe not so fast. 424.4(B) says the branch circuit conductors shall be sized at 125% of the rating of the heater load. What about the OCPD? Can a 50 amp OCPD be used with #6 conductors? 424.4(A) seems to say that the OCPD can be 50 amps for this load. Obviously if you've already run 65 amp conductors it would be easy to simply use a 60 amp OCPD but is it required if the load is non-continuous? Also for this installation no NM cable will be used.
424.4(B) Branch-Circuit Sizing.
The branch-circuit conductors for fixed electric space-heating equipment and any associated motors shall be sized not smaller than 125 percent of the load.
424.4 Branch Circuits.
424.4(A) Branch-Circuit Requirements.
An individual branch circuit shall be permitted to supply any volt-ampere or wattage rating of fixed electric space-heating equipment for which the branch circuit is rated.