- Location
 - New Jersey
 
- Occupation
 - Journeyman Electrician (retired)
 
Someone asked me today about the branch circuit for a 10kw, 240 volt, thermostatically controlled electric garage heater.  I immediately said 60 amp circuit.  Then when I looked in the codebook I thought well maybe not so fast.  424.4(B) says the branch circuit conductors shall be sized at 125% of the rating of the heater load.  What about the OCPD?  Can a 50 amp OCPD be used with #6 conductors?  424.4(A) seems to say that the OCPD can be 50 amps for this load.  Obviously if you've already run 65 amp conductors it would be easy to simply use a 60 amp OCPD but is it required if the load is non-continuous?  Also for this installation no NM cable will be used.
	
		
			
		
		
	
				
			424.4(B) Branch-Circuit Sizing.
The branch-circuit conductors for fixed electric space-heating equipment and any associated motors shall be sized not smaller than 125 percent of the load.
424.4 Branch Circuits.
424.4(A) Branch-Circuit Requirements.
An individual branch circuit shall be permitted to supply any volt-ampere or wattage rating of fixed electric space-heating equipment for which the branch circuit is rated.
				