I have a 100A fused switch the utility company wants me to add for solar. The feeder is circled in yellow in attached photo. The client is picky and I thought I would ask for suggestions for routing?
It's 1/0 Wire.
Thanks
That is what I was going to mention, there isn't much you can do to this to make it look worse than it already does.What's the client picky about? The current setup already looks atrocious.
Thanks, I am concerned about digging there, are there rules regarding crossing the other conduit with deep strut,as ppsh says above?Punch a 1- 1/4inch hole between the two 3/4 inch nipples that are entering the cabinet from the bottom.
Go all the way to the bottom--dig a shallow trench and come up to the side of the timer. You will need two 90s for this. This way you would not be crossing those existing conduits.
Mount the 100A disconnect right above the irrigation timer.
To appease the picky client--frame the fused disconnect with a picture frame that was yanked out of a Mona Lisa portrait copy.
Just kidding. . .disregard the picture frame bit and do the first three paragraphs.