mwm1752
- Aspen, Colo
210.70 Lighting Outlets Required
(1) Habitable Rooms. At least one wall switch–controlled lighting outlet shall be installed in every habitable room and bathroom.
Exception No. 2: Lighting outlets shall be permitted to be controlled by occupancy sensors that are (1) in addition to wall switches or (2) located at a customary wall switch location and equipped with a manual override that will allow the sensor to function as a wall switch.
Just wondering -- the requirement is for a "wall switch–controlled lighting outlet" which does not designate a location for the switch but only for the lighting outlet -- The Exception No.2: uses language " located at a customary wall switch location " for a descriptive location if the occupancy sensor is the only control for the lighting outlet.
There is no requirement to install a switch inside the specified rooms in fact they could be anywhere in the building and it does make sense to install motion detectors inside the room -- but it seems to me describing a location as customary for a motion dectecting switch has association to the wall mount switch requirement.