You would need to read the spec sheet. Some require shielded twisted pairs, but it's never just 'telephone' cable.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
You would need to read the spec sheet. Some require shielded twisted pairs, but it's never just 'telephone' cable.

Ok I meant cat 5 or 6 or I guess shielded TWP. But that is for telephone which I am asking does it need one of those lines as well as cable(fire alarm circuit) to the FACP or DGP etc.? What i am asking is do they always get a cable or cables for telephone and one for fire alarm whatever they may be in the spec? Thanks.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Typically just a single pair F/A cable, as mentioned the vendor might require shielded cable.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Typically just a single pair F/A cable, as mentioned the vendor might require

Ok thanks just did not think the phone function communicated over f/a cables

Usually they are driven by a telephone zone card in the voice portion of the fire alarm/voice evac panel. They may, depending on the spec and/or AHJ requirements, have to be wired using circuit integrity cable.
 