Are they wired with both fire alarm cable and telephone cable? Thanks.
You would need to read the spec sheet. Some require shielded twisted pairs, but it's never just 'telephone' cable.
Typically just a single pair F/A cable, as mentioned the vendor might require
Ok thanks just did not think the phone function communicated over f/a cables
Typically just a single pair F/A cable, as mentioned the vendor might require
Ok thanks just did not think the phone function communicated over f/a cables
Usually they are driven by a telephone zone card in the voice portion of the fire alarm/voice evac panel. They may, depending on the spec and/or AHJ requirements, have to be wired using circuit integrity cable.
Usually they are driven by a telephone zone card in the voice portion of the fire alarm/voice evac panel. They may, depending on the spec and/or AHJ requirements, have to be wired using circuit integrity cable.
Actually it's been a long time since I've installed one.