S Squiggy969 Member Location PA Occupation Underwriter Dec 8, 2024 #1 210.8b8 2017 nec explains areas that require gfci protection. Warehouses are not mentioned anywhere unless the code is considering them "similiar" areas.
210.8b8 2017 nec explains areas that require gfci protection. Warehouses are not mentioned anywhere unless the code is considering them "similiar" areas.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Dec 8, 2024 #2 There is no requirement for GFCI protection in a warehouse.
Fred B Senior Member Location Upstate, NY Occupation Electrician Dec 8, 2024 #3 don_resqcapt19 said: There is no requirement for GFCI protection in a warehouse. Click to expand... other than within 6 ft of a sink 210.8(B)(5)
don_resqcapt19 said: There is no requirement for GFCI protection in a warehouse. Click to expand... other than within 6 ft of a sink 210.8(B)(5)
kwired Electron manager Location NE Nebraska Occupation EC Dec 8, 2024 #4 Fred B said: other than within 6 ft of a sink 210.8(B)(5) Click to expand... Or if it were a wet location or happened to be outdoors, or at least in any portions where those characteristics apply.
Fred B said: other than within 6 ft of a sink 210.8(B)(5) Click to expand... Or if it were a wet location or happened to be outdoors, or at least in any portions where those characteristics apply.