I made a statement in this thread earlier that if you are upgrading an electrical service you are not required to put MWBC's on a 2-pole breaker (at least it's that way in NJ as far as I know).
WELL, an EI at a residential inspection today said I was wrong and stated that as long as l upgraded from 100A service to a to 200A service I was required to do so. I stated my case that I did not change the existing wiring and that the MWBC was originally on separate breakers. I was replacing like with like. Here's the kicker - he said that the KEY word was UPGRADE. I went from 100A to 200A service. If I had merely REPLACED ALL the service equipment and installed a new 100A service I would not have to install a 2-pole breaker - That's not considered an UPGRADE. You can't make this stuff up folks.
I also used SE cable and installed the weather-head about 16-18" above the porcelain insulator on the rake of the house. My intent was to keep the drip loop at least 3' away from the window below. He stated that the weather-head had to be no more than 12" from the point of attachment (he said it's in the NEC - I can't find it). Anyway, not to burn a bridge with this guy I installed a new porcelain insulator about 6" away from the weather-head.
Finally, I had installed a #4 ground wire to the water main. Here in NJ we are required to bond across the water meter. So, I installed a CONTINUOUS #4 wire through the 1st pipe clamp which was on the house side of the meter and then to the pipe clamp on the street side of the meter. He stated that I had to hit the street side first and then the house side. So, I high-press crimped another piece of # 4 to the existing wire on the street side of the water main and then to another pipe clamp on the house side. Now my installation officially looks like crap.
2017 code cycle and AFCI for panel replacement
I have a pretty good handle on AFCI requirements for 2017 but have a question related to panel and service changes our area uses 2017 code. There are many jobs in the area for aerial service changes due to age. If you change from the weather head down and replace old panel with new are you...
forums.mikeholt.com
WELL, an EI at a residential inspection today said I was wrong and stated that as long as l upgraded from 100A service to a to 200A service I was required to do so. I stated my case that I did not change the existing wiring and that the MWBC was originally on separate breakers. I was replacing like with like. Here's the kicker - he said that the KEY word was UPGRADE. I went from 100A to 200A service. If I had merely REPLACED ALL the service equipment and installed a new 100A service I would not have to install a 2-pole breaker - That's not considered an UPGRADE. You can't make this stuff up folks.
I also used SE cable and installed the weather-head about 16-18" above the porcelain insulator on the rake of the house. My intent was to keep the drip loop at least 3' away from the window below. He stated that the weather-head had to be no more than 12" from the point of attachment (he said it's in the NEC - I can't find it). Anyway, not to burn a bridge with this guy I installed a new porcelain insulator about 6" away from the weather-head.
Finally, I had installed a #4 ground wire to the water main. Here in NJ we are required to bond across the water meter. So, I installed a CONTINUOUS #4 wire through the 1st pipe clamp which was on the house side of the meter and then to the pipe clamp on the street side of the meter. He stated that I had to hit the street side first and then the house side. So, I high-press crimped another piece of # 4 to the existing wire on the street side of the water main and then to another pipe clamp on the house side. Now my installation officially looks like crap.