Guys and Girls -
I'm not seeing much of an issue here. There is risk in everything we do. Why is this one different?
JAO: The NEC requirement is a near useless label, required since the 2002. The real issue is the OSHA requirement for the workers to understand the risks.
jcook980 said:
If Washington expects the engineer to provide these calculations, the cost of my projects in Washington will have to go up
Yes - and ....?
don_resqcapt19 said:
...With the major issue of getting "real" available fault current information from the utility, I would never sign my name to a calculation like that...
Then I would ask, How do you meet 110.9 and 110.10? I'm not seeing a lot of difference.
don_resqcapt19 said:
...Too much future liability. I expect that as soon as the professional liability insurance companies find this out, there will be a very expensive ridder to do this type of calcualtion...
We are doing the calcs now and have been for a few years, and as far as I know there are no expensive riders yet. Then again, my crystal ball isn't nearly as sharp as yours, and tomorrow is a new day. But, what ever surcharge there is, jcook980 knows how to handle it - and so do I.
ron said:
...Is the AHJ requiring the generic arc flash label required in the NEC, or the detailed calculation label recommended in the standard 70E.
NFPA 70E is not enforceable by the AHJ unless the local jurisdiction has adopted it as code, and I was not aware of any that have.
ron is absolutely right-on. The generic NEC required label is pretty benign. NFPA 70E is not law. It is however a useful standard and if followed, is an excellent defensible position.
dlhoule said:
... we can get available fault current available from utility. ...you can plug a few numbers into a formula to come up with Arc Flash numbers. ... Our labels show the hazard level and the required PPE...
Another great response. It meets my understanding of NFPA 70E, Annex D. The IEEE papers on arcflash are a little more complex than "plug a few numbers", but the concept is still right-on.
don_resqcapt19 said:
...The problem is that a lower available fault current often results in a higher incident energy level ...
I've heard this plenty, but I don't know where it comes from. I could see it if one used the term, "could possibly", instead of "often". Incident energy is porportional to I^2t. so if the current dropped to 70%, the clearing time would have to double to keep the same incident energy (NFPA 70E, Annex D, 600V example) Checking the upper and lower bounds and setting appropriate protective settings is necessary and certainly part of the engineering.
jcook980 said:
...If we did arc flash studies during design, they would be incorrect as we have little control over contractor selections for OCPD, transformer impedances
As I mentioned earlier: Why is this different than 110.9 or 110.10?
dlhoule said:
...Slight misunderstanding on my part...
I don't think so, I think you are right on
Some other engineers think there is too much liability - okay with me. As far as me doing the work - sure I would. Follow existing codes and standards. Do the research. State the limitations. Pay the insurance. Charge what the traffic will bear. Where is the difference from this to anything else we do?
carl