jmellc
Senior Member
- Location
- Durham, NC
- Occupation
- Facility Maintenance Tech. Licensed Electrician
Had a service call where microwave kept going out. Sometimes tripped breaker, sometimes not. Kept hearing a click sounding like coming from crawl space, sounded like a breaker tripping. Went under & found no other load on the ckt & no OC device. Checked again & found the recep was 2nd in line. 1st had been back stabbed & wires were very loose. Still gave a good voltage reading, on that recep & the others downline. A blender worked fine on the ckt, smaller load. But the MW was causing wires to vibrate a little & flicker. That put MW into reset mode. I pigtailed the recep & others downline too. No more problem. Look for this if you get a strange acting microwave.