NFPA 72 requires only that a waterflow alarm device be provided. The kicker comes from NFPA 13 which requires an alarm device be provided and that it continue to sound until the waterflow stops (3-10.1) If someone silences the panel and the NAC the waterflow alarm device is on isn't or can't be set as non-silenceable, you would violate the requirements of NFPA 13. Easier to grab a handy 120 VAC line and wire it up.
Oddly enough, on a quick look, it doesn't appear that this device is required to be supervised in either NFPA 13 or 72. In fact, if the waterflow alarm device is electrically operated and is NOT part of a required protective signaling system, it shall not be supervised per 3-10.5.1 and shall be installed per NFPA 70 article 760. It is possible that "supervised" in this context means sending a signal to a "contstantly attended location" but I wouldn't swear to that.
Oddly enough, on a quick look, it doesn't appear that this device is required to be supervised in either NFPA 13 or 72. In fact, if the waterflow alarm device is electrically operated and is NOT part of a required protective signaling system, it shall not be supervised per 3-10.5.1 and shall be installed per NFPA 70 article 760. It is possible that "supervised" in this context means sending a signal to a "contstantly attended location" but I wouldn't swear to that.