Having a slight disagreement with the AHJ on where the ground from the water and gas main should terminate.
200A service to meter pedestal, 200A OCPD outside next to meter, conduit to tap box inside, 2 OCPDs 100A each with SER runs to two 100A panels. One panel is on a standyby generator, one isnt.
AHJ wants it in the meter box or first OCPD. I want to put it in the tap box, or at one of the secondary OCPD. One of the OCPDs is about 6' from both the water and gas mains. The GEC runs out of the 200A OCPD to the rods.
Am I forced to run all the way back to the main OCPD?
200A service to meter pedestal, 200A OCPD outside next to meter, conduit to tap box inside, 2 OCPDs 100A each with SER runs to two 100A panels. One panel is on a standyby generator, one isnt.
AHJ wants it in the meter box or first OCPD. I want to put it in the tap box, or at one of the secondary OCPD. One of the OCPDs is about 6' from both the water and gas mains. The GEC runs out of the 200A OCPD to the rods.
Am I forced to run all the way back to the main OCPD?